RSTP between Catalyst Switch and MS Switch

Solved
meraki-newbie
Getting noticed

RSTP between Catalyst Switch and MS Switch

Dear All,

 

We want to make catalyst switch(Core) below as an RSTP root primary and secondary for several MS switches under the Core :

 

merakinewbie_0-1717838286730.png

 

 

We have already state the all the MS switch RSTP priority to the maximum value of 61140

 

merakinewbie_2-1717838425201.png

 

 

but, it seems the root switch still on each MS

 

merakinewbie_1-1717838362603.png

 

is there any approaches to move the RSTP root to the Catalyst Core Switch, below a brief config on catalyst

 

 

merakinewbie_3-1717838503593.png

 

 

 

glad to hear any response from you all

1 Accepted Solution
IvanJukic
Meraki Employee
Meraki Employee

Hi @meraki-newbie ,

 

As others have mentioned, it is recommended to run Multiple Spanning Tree on the Catalysts. As it is built upon IEEE 802.1D & IEEE 802.1w

 

You can achieve interoperability with RSTP & Rapid-PVST. However, it requires careful planning and configuration. See below excerpt from the guide below.

 

https://documentation.meraki.com/MS/Deployment_Guides/Advanced_MS_Setup_Guide#Protocol_interoperabil...

 

‘MS series switches can participate in spanning tree only when a spanning tree instance is running on Native VLAN of ALL switches. In addition, Native VLAN must be allowed on all Trunk ports running Rapid-PVST, so that BPDUs are seen by the Meraki switches in the topology.’

 

 

 


Cheers,

Ivan Jukić,
Meraki APJC

If you found this post helpful, please give it kudos. If it solved your problem, click "accept as solution" so that others can benefit from it.

View solution in original post

11 Replies 11
ww
Kind of a big deal
Kind of a big deal

Most convert to mstp on catalyst with meraki for stability.

 

But Rstp-rpvst should also work, it runs on  native vlan. (Doc says vlan1) https://documentation.meraki.com/MS/Port_and_VLAN_Configuration/Configuring_Spanning_Tree_on_Meraki_...

Do you have a trunk with native vlan on both sides?

meraki-newbie
Getting noticed

so for stability we need to configgure mstp on catalyst?

 

yes we have already run native vlan 99 between ms <> catalyst trunk ports

 

but the root port not appearing at Catalyst, as we expected

DarrenOC
Kind of a big deal
Kind of a big deal

As per the note in the document provided by @ww switch to mst:

 

Note: To avoid unexpected issues where an MS is between two R-PVST switches (such as a Cisco Catalyst Root Bridge < MS > Catalyst switch). It is recommended to convert the topology to a MSTP on the Catalyst switches. This will avoid potential port inconsistency errors and other issues that may cause instability in the STP topology.

 

 

Darren OConnor | doconnor@resalire.co.uk
https://www.linkedin.com/in/darrenoconnor/

I'm not an employee of Cisco/Meraki. My posts are based on Meraki best practice and what has worked for me in the field.
meraki-newbie
Getting noticed

Alright,

 

so, with this topology below

 

MX1-MX2

|.           |

CAT1-CAT2

      \.   /

   MS125

 

we should set MSTP between 2 CATALYST (CAT1 & CAT2) setup the CAT1 as root & CAT2 as secondary root.. 

 

meanwhile on the MS125, just config RSTP with highest number priority available, so the forwarding path will be

 

CAT1-CAT2 

MS125-CAT1

 

 

and the blocking path will be

 

MS125-CAT2

 

is my understanding of the concept correct?

RaphaelL
Kind of a big deal
Kind of a big deal

CAT1 and CAT2 are not in a VSS configuration ?

meraki-newbie
Getting noticed

for now we didn't use the VSS between CAT1-CAT2 (WSC3850)... should we set VSS the CAT1-CAT2 for better results?

 

 

RaphaelL
Kind of a big deal
Kind of a big deal

I couldn't see the model from your screenshot. These switches do not support VSS

IvanJukic
Meraki Employee
Meraki Employee

Hi @meraki-newbie ,

 

As others have mentioned, it is recommended to run Multiple Spanning Tree on the Catalysts. As it is built upon IEEE 802.1D & IEEE 802.1w

 

You can achieve interoperability with RSTP & Rapid-PVST. However, it requires careful planning and configuration. See below excerpt from the guide below.

 

https://documentation.meraki.com/MS/Deployment_Guides/Advanced_MS_Setup_Guide#Protocol_interoperabil...

 

‘MS series switches can participate in spanning tree only when a spanning tree instance is running on Native VLAN of ALL switches. In addition, Native VLAN must be allowed on all Trunk ports running Rapid-PVST, so that BPDUs are seen by the Meraki switches in the topology.’

 

 

 


Cheers,

Ivan Jukić,
Meraki APJC

If you found this post helpful, please give it kudos. If it solved your problem, click "accept as solution" so that others can benefit from it.
meraki-newbie
Getting noticed

It works

 

the root bridge of MS125 is our Catalyst C3850 core..

 

we set up MSTP between C3850 .. 

 

Core 1 MSTP priority 4096

Core 2 MSTP priority 8192

All MS125 RSTP priority 61140

 

thanks all.. 

 

IvanJukic
Meraki Employee
Meraki Employee

Nice!!!!! Well done!.




Cheers,

Ivan Jukić,
Meraki APJC

If you found this post helpful, please give it kudos. If it solved your problem, click "accept as solution" so that others can benefit from it.
annmarie24us
Meraki Employee
Meraki Employee

I agree with Ivan that ‘MS series switches can participate in spanning tree only when a spanning tree instance is running on Native VLAN of ALL switches. In addition, Native VLAN must be allowed on all Trunk ports running Rapid-PVST, so that BPDUs are seen by the Meraki switches in the topology.’