UPS for MS Switches
Hi All,
We are looking at purchasing the below MS switches;
8x MS425-16
9x MS225-48LP
2x MS350-24X
Anyone who would recommend good UPS units for me?
Do the switches come with a single power supply, or are there redundant power supplies?
Currently, I am assuming we have a single power supply = 480W peak power consumption.
Solved! Go to solution.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi @Riser , all switches will ship with a single power supply. You can however buy a secondary power supply for the 425 (MA-PWR-250WAC). and 350-24x (MA-PWR-1025WAC). The 225 would require an external RPS for power backup (PWR-RPS2300)
https://www.linkedin.com/in/darrenoconnor/
I'm not an employee of Cisco/Meraki. My posts are based on Meraki best practice and what has worked for me in the field.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi @Riser , all switches will ship with a single power supply. You can however buy a secondary power supply for the 425 (MA-PWR-250WAC). and 350-24x (MA-PWR-1025WAC). The 225 would require an external RPS for power backup (PWR-RPS2300)
https://www.linkedin.com/in/darrenoconnor/
I'm not an employee of Cisco/Meraki. My posts are based on Meraki best practice and what has worked for me in the field.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Hi Ucert,
Thanks for your prompt response. Do you know if it's possible to combine 2 power supplies on the MS switches to ensure redundancy in case of an outage? I'm looking at having one power cable go directly to a switch from the main circuit and the second power cable go through a UPS.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
Morning, where you can have dual power supplies ie the MS350 and 425 there’s no reason why you could t have one connected to a UPS and the other via a main circuit.
https://www.linkedin.com/in/darrenoconnor/
I'm not an employee of Cisco/Meraki. My posts are based on Meraki best practice and what has worked for me in the field.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
To add further to this, I don't know that I would connect an MS switch (or any other networking equipment) direct to an outlet without a UPS. In addition to power, they also provide line conditioning and surge protection. In a dual power supply switch, in an ideal environment, each one connects to a different UPS.
School and Church
K-12 Education
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
@Riser as @DarrenOC mentioned you can connect one PSU to a UPS and the other directly too mains or to a different UPS. If possible as well as having redundant power supplies having redundant power if you can is a good fallback.