STP - Stopped receiving BPDUs with loop guard enabled

Solved
Sweemz
Here to help

STP - Stopped receiving BPDUs with loop guard enabled

Hi All,

 

I hope we are well.

 

I’ve recently inherited a Cisco Meraki network following an acquisition and have noticed some alerts.

 

Edit - Added Network Topology/Switch overview (below)

 

Toplogy

Sweemz_0-1737623756757.png

 

Switch Overview

Sweemz_1-1737623942455.png

 

 

Sweemz_0-1737580717988.png

 

The network Consists of:

2 x MX105 in HA config.

5 x MS130-48P 

4 x CW9166I


I've documented the network as best as possible..
(minus the access points) will re-review tomorrow and update asap.

 

Version 1

Sweemz_1-1737580780911.png

 

Version 2 - Since Reviewing Meraki Live Topology

- Root Ports mislabelled / corrected 

Sweemz_0-1737625704971.png

 

 

DUG00-SW01 Port 51 

Sweemz_2-1737580917103.png

Sweemz_3-1737581077005.png

 

DUG00-SW03 Port 50

Sweemz_4-1737581257527.png

 

Sweemz_6-1737581286390.png

 

The affected ports seem to be alternate uplink ports, so the network is still operational. I’d just like to understand the issue and get the network’s RAG status back to healthy.

 

Any thoughts on the best place to start troubleshooting?

 

Thanks in advance - let me know if you need more information!

 

1 Accepted Solution
RWelch
Head in the Cloud
Head in the Cloud

Not sure why 3 downlinks are needed….seems a bit overkill or over engineered.  

 

Too many redundant paths likely intended for a failover situation but the errors seem to be the redundant paths (3 downlinks).

 

If it were my network to remedy, each switch would have only two downlinks with all root traffic from SW00.


SW01 and SW02 would be one alt path (loop guard)

SW03 and SW04 would be one alt path (loop guard)

 

I would remove the link between SW02 and SW03.

I would remove the link between SW01 and SW04.

 

Thanks for sharing the topology to better understand. 
That would be my suggestion/recommendation. 

If you found this post helpful, please give it Kudos. If my answer solves your problem please click Accept as Solution so others can benefit from it.

View solution in original post

19 Replies 19
RWelch
Head in the Cloud
Head in the Cloud

I realize you mentioned inheriting this network but the device health notice indicates SW01 and SW03 error notices yet the lower images you share indicate SW04 and the port descriptions don’t seem to jive.  Seems like something doesn't quite add up.

If you found this post helpful, please give it Kudos. If my answer solves your problem please click Accept as Solution so others can benefit from it.
RWelch
Head in the Cloud
Head in the Cloud

Can you share a screen capture of the topology from the meraki dashboard to see what that shows....I'm curious to see if that might reveal more insight.  Not meant as critical at / toward you....just tried to understand the above and I looked at it like 10 times.

If you found this post helpful, please give it Kudos. If my answer solves your problem please click Accept as Solution so others can benefit from it.
IvanJukic
Meraki Employee
Meraki Employee

Hi @Sweemz ,

 

Not sure I follow the Topology Diagram either. Port 52 is directly connected to the Root switch. So that would be the Root port. Port 49 & 50 would be alternate ports.


I agree with @RWelch. The Topology map in the Dashbaord is 'live". So if the Tree changes so will the map. I use it daily. Best tool to use for these kind of queries.

 

https://documentation.meraki.com/MS/Monitoring_and_Reporting/Network_Topology

If you can share a screenshot, that'll be helpful.


Cheers,

Ivan Jukić,
Meraki APJC

If you found this post helpful, please give it kudos. If it solved your problem, click "accept as solution" so that others can benefit from it.
Sweemz
Here to help

Hi @IvanJukic 

 

Thank you for looking into this.

 

2nd glance i've clearly made some mistakes with my labels 😅

Using the Network topology tool I have re-confirmed the uplinks/ports and updated my documentation to reflect the live links in the Meraki Toplogy.

 

Sweemz_0-1737625324266.png

 

 

Sweemz_1-1737625371887.png

 

Sweemz_2-1737625385422.png

 

IvanJukic
Meraki Employee
Meraki Employee

No problem at all @Sweemz

Given the devices have already been purchased you could increase efficiency and redundancy. My preference would be to clean up the design, rather than chasing errors and warnings. 

Judging by that Topology Screenshot. It Seems like, RSTP Priority is set to the default of 32768, and SW00 happens to be the Root Bridge. However, without actually looking into the Network, I can't verify.

Also, it looks like SW01 could be a Backup Root or potentially used as one. If so you could have; 

 

A) SW00 & SW01 connected together as a Core/Distribution. With uplinks to the MX-HA Pair.

B) SW00 as Root Priority 0
C) SW01 backup Priority 4096

D) SW02,3,4 leave Priority as is. Then only have 2 uplinks, 1 each to SW00 & SW01.

E) All other Devices connected to only SW02,3,4

 

 


Cheers,

Ivan Jukić,
Meraki APJC

If you found this post helpful, please give it kudos. If it solved your problem, click "accept as solution" so that others can benefit from it.
Sweemz
Here to help

Not sure why I didn't include these originally 😅 .. Thank you for looking into this btw

 

Toplogy

Sweemz_0-1737623756757.png

 

Switch Overview

Sweemz_1-1737623942455.png

 

RWelch
Head in the Cloud
Head in the Cloud

Not sure why 3 downlinks are needed….seems a bit overkill or over engineered.  

 

Too many redundant paths likely intended for a failover situation but the errors seem to be the redundant paths (3 downlinks).

 

If it were my network to remedy, each switch would have only two downlinks with all root traffic from SW00.


SW01 and SW02 would be one alt path (loop guard)

SW03 and SW04 would be one alt path (loop guard)

 

I would remove the link between SW02 and SW03.

I would remove the link between SW01 and SW04.

 

Thanks for sharing the topology to better understand. 
That would be my suggestion/recommendation. 

If you found this post helpful, please give it Kudos. If my answer solves your problem please click Accept as Solution so others can benefit from it.
Sweemz
Here to help

Thank you @RWelch 

 

Makes absolute sense.

 

I'll have a play with this network this evening and provide an update on the topology asap.

RaphaelL
Kind of a big deal
Kind of a big deal

APs do not participate to the STP topology so that shouldn't matter 

annmarie24us
Meraki Employee
Meraki Employee

I agree with RWelch too many redundant paths for the failover situation and the errors do seem to be the redundant 3 paths.  

 

I see you are on MS 16.9 and there is an update firmware for these switches as well MS 17+ would help as well.

Sweemz
Here to help

Update - 27/01/25

 

2 x Links have been removed

  • Link between SW02 and SW03
  • Link between SW01 and SW04.

 

Updated Topology

Sweemz_2-1737993855100.png

 

Observation

Alert on DUG00-SW01 has disappered

Alert on DUG00-SW04 persists

 

Sweemz_1-1737993537241.png

 

Going to attempt port cycles on DUG00-SW03, Port 50 & DUG00-SW04, Port 49 to see if it gives it a kick. If the Alert persists I will also try a reboot of switches this evening to see if this clears out the alert.

 

IF all goes well I will then schedule in a FW update later this week.

 

RWelch
Head in the Cloud
Head in the Cloud

If an error or alert remains, I could simply double check the following port STP guard settings: 

STP Guard setting between SW01 and SW02 ports (on both switches) would be loopback guard.

STP Guard setting between SW03 and SW04 ports (on both switches) would be loopback guard.

 

STP Guard setting (uplink) on SW01, SW02, SW03 and SW04 going up to SW00 would all be disabled.

 

STP Guard setting (downlink) on SW00 going down to SW01, SW02, SW03 and SW04 would all be root guard.

 

And as @IvanJukic mentioned, setting the SW00 as bridge prioirity 0.  I would personally set all the other switches (SW01-SW04) at root bridge priority of 61440, however he mentioned leaving at the default 32768 (he might know something that I don't in that regard).

Dashboard > Switching > Configure > Switch Settings where you can set STP Configuration (STP bridge priority)

If you found this post helpful, please give it Kudos. If my answer solves your problem please click Accept as Solution so others can benefit from it.
Sweemz
Here to help

Thanks @RWelch I can confirm that the STP Guard settings are configured exactly as you suggested/described.

 

For the STP bridge priority I have DUG00-SW00 configured as '4096' and then anything else falls under the default of '32768'.

 

Sweemz_0-1738239793128.png

 

Should I explicitly define all other switches in here as a higher priority e.g '32768'? All other switches do show DUG00-SW00 as the RSTP root. 

RWelch
Head in the Cloud
Head in the Cloud

SetBridgePriority.png
In following the best practices, the Configuring Spanning Tree on Meraki Switches (MS) document indicates, "At no point in a production network should you leave the any switch at its default configurations."

If you found this post helpful, please give it Kudos. If my answer solves your problem please click Accept as Solution so others can benefit from it.
Sweemz
Here to help

Thank you @RWelch reading up now. Will look to action later today and will provide an update asap.

hanjo
New here

It looks like you’ve done a great job documenting everything so far! Since the affected ports are alternate uplinks, I’d start by checking STP settings, port roles, and any recent config changes. Have you noticed any looping or high latency issues?

Sweemz
Here to help

@hanjo thank you.

 

Just done a review of the STP settings (see recent RWelch comment/my response) - all appears correct.

 

No looping and or high latency issues observed and or reported, no issues with connectivity/routing etc - the network is working, it's just alerting 🤷‍

Sweemz
Here to help

Update as of 19:30 | 04/02/25 -

 

I'm happy to report that he remaining 'stp_loopguard_active' alert that was displaying for SW03 is now resolved 🙂

Sweemz_0-1738697984045.png

Sweemz_1-1738698571968.png

 

Looks like the Frimware Upgrade to MS 17.1.4 gave the switches a kick/reset.

 

Now.. for credit where credit is due, thank you to everyone that responded, this was a great experience for me on the Meraki forum. 

 

Thank you for your time and for sharing your knowledge! 🫡

 

RWelch
Head in the Cloud
Head in the Cloud

👏 👏 👏

If you found this post helpful, please give it Kudos. If my answer solves your problem please click Accept as Solution so others can benefit from it.
Get notified when there are additional replies to this discussion.
Welcome to the Meraki Community!
To start contributing, simply sign in with your Cisco ID. If you don't yet have a Cisco ID, you can sign up.
Labels