Hi @Noffal
Again, the chassis side of the cable (MA-PWR-CORD-*) is C15. And the inlet on the MX95 chassis side is C14. Not C13. Physical talk can connect.
The C15 connector is designed to connect to the C14 and C16 inlets. IEC standard. There are C14 and C16 models on the Meraki Power supply module side, but the cable (MA-PWR-CORD-*) can be connected to both in common. Since it has been officially verified by Meraki in the first place, the MA-PWR-CORD-* will definitely connect. 3rd Party? Self-responsibility.
Power Cord Types, Power Cable types, Power Plug types | FS Community
A C13 connector cannot be connected to a C16 inlet. Because it is designed to exceed the temperature rating of C13/C14, there is a notch in C13/C14 so that it cannot be inserted because it is dangerous.