Hi Team,

I’m looking for the power supply minimum output hold-up time for some Meraki devices (MS and MX).

The customer is using UPS Interactive Line and the time to switch power from generator and UPS is about 6-10 ms so we want to know if the Meraki devices will restart or not.

Thank you!

Best Regards,
Kane

5 REPLIES 5
PhilipDAth
Kind of a big deal
Kind of a big deal

I don't know thw answer.

 

That is about 1/4 to 1/2 wave.  I would think you should be ok with that.

Kane
Comes here often

Thanks @PhilipDAth though!

I was hoping to provide a confirmed answer along with a documentation as well. I'm also concerned if the device's load is also a factor.

Hopefully someone from Meraki can help answer this.
PhilipDAth
Kind of a big deal
Kind of a big deal

There is no such information published.

 

The only way to get assurance if this is very important will be to change to a double online interactive UPS.  Plus it will provide the equipment with much more protection during the generator startup.

Found something interesting.  Several of the MS's support using an RPS2300 for redundant power.  It specifies the hold up time that it offers in the event of primary power supply failure.

https://www.cisco.com/c/en/us/products/collateral/switches/redundant-power-system-2300/product_data_... 

 

Table 2.       Power Supply Specifications

Description

Specification

C3K-PWR-1150WAC

C3K-PWR-750WAC

Maximum output power

1150W

750W

Input-voltage range and frequency

115-240 VAC, 50-60 Hz

100-240 VAC, 50-60 Hz

Input current

12-6A

10-5A

Output ratings

12V@25A and -52V@16.4A

12V@25A and -52V@8.7A

Output holdup time

20 ms minimum

20 ms minimum

Power-supply input receptacles

IEC 320-C13 (IEC60320-C13)

IEC 320-C13 (IEC60320-C13)

Power cord rating

15A

15A

LED indicators

“AC OK” - Input power to the power supply is working properly

“PS OK” - Output power from the power supply is working properly

Kane
Comes here often

I'm aware of those information for the RPS 2300. However, this is only applicable if the customer is using RPS 2300 on their MS switches as backup power.

Thanks @PhilipDAth for your help though! 🙂